Temperature probe is a resistance type probe. Check the probe resistance across the cables connected to the inverter terminals after disconnecting them from the terminal.

  • For d series compressor reading should be in between 900 ohms to 1500 ohms
  • For x series compressor reading should be in between 90 ohms to 150 ohms.
    Out of this values probe or cable is damaged.
Reason Solution
Temperature Sensor Failure Check temperature sensor cable, make sure cables are not cut and properly connected to PLC.If cabling are correct and not damaged, change temperature sensor